250 likes | 853 Views
IEC 62271-100 Short-circuit current making and breaking tests Taiwan-European HVAC apparatuses Accreditation and Certification forum. Harethe El Ouadhane IEC Expert: Member of MT14 of IEC62271-200 Testing , design & calculation / MVSG & MVCB
E N D
IEC 62271-100Short-circuit current making and breaking testsTaiwan-European HVAC apparatusesAccreditation and Certification forum Harethe El Ouadhane IEC Expert: Member of MT14 of IEC62271-200 Testing, design & calculation / MVSG & MVCB Expert for internal arc, making, breaking and STC
Content • Requirements of IEC 62271-100 • Basic short-circuittestduties • Single-phase fault tests • Double-earth fault tests • Technology ofvacuuminterrupters • Extension of the validity of test results and derivations • Conclusion
1. Requirements of IEC 62271-100 • Mandatory TestCircuit-breakers shall be capable of making and breaking all short-circuit currents, symmetrical and asymmetrical, up to and including the rated short-circuit breaking currents: This is demonstrated, when the circuit-breakers make and break the specified three-phase symmetrical and asymmetrical currents between 10% (T10) and 100% (T100) of the rated short-circuit breaking current at rated voltage. • In additionCircuit-breakers shall be capable of clearing single-phase short-circuit currents which may occur in two different cases:– in effectively earthed neutral systems in case of single-phase faults or,– in non-effectively earthed neutral systems in case of double earth faults, i.e. earth faults on two different phases, one of which occurs on one side of the circuit-breaker and the other one on the other side.
2. Basic short-circuittestduties • Number of test specimena unique test specimen should be used. Where required, maintenance is allowed and should be performed as permitted, between each individual test-duty in the case of short-circuit tests The manufacturer shall provide a statement to the testing laboratory of those parts that may be renewed during the tests. • No-load testBefore commencing making and breaking tests, no-load operations and no-load operating sequences (O, CO and O – t – CO) shall be made and details of the operating characteristics of the circuit-breaker recorded. Details such as closing time and opening time shall be recorded.
2. Basic short-circuittestduties • Behavior of circuit-breaker during testsDuring making and breaking tests, the circuit-breaker shall not– show signs of distress;– show harmful interaction between poles and to earth;– show harmful interaction with adjacent laboratory equipment;– exhibit behavior which could endanger an operator. NSDDs may occur during the recovery voltage period following a breaking operation • Condition after a short-circuit test-duty After each short-circuit test-duty, the circuit-breaker shall be capable of making and breaking its rated normal current at the rated voltage, although its short-circuit making and breaking performance may be impaired.
2. Basic short-circuittestduties • FrequencyCircuit-breakers shall be tested at rated frequency with a tolerance of ±8 %. However, for convenience of testing, some deviations from the above tolerance are allowable; for example, when circuit-breakers rated at 50 Hz are tested at 60 Hz and vice versa, care should be exercised in the interpretation of the results, taking into account all significant facts such as the type of the circuit-breaker and the type of test performed.
2. Basic short-circuittestduties • There are several requirements for the test circuit, test parameters and CB • arrangements in order to simulate the possible worst case switching of the • CB in real system. • In general, closing against the highest making current, opening with • various arcing times and recovery voltages, under the unfavourable • mechanical operating conditions. • The main ones are among others related to: • Operating sequence O – CO – CO, with or without auto-reclosingT10, T30, T60, T100s & only O for T100a, SPF & DEF • Factors for recovery voltages; first-pole-to-clear (neutral earthing) and amplitude factor (based on CIGRE), RRRV • Arcing time and arcing window: Depending on the point of mechanical contact separation, interruption with minimum, medium and maximum arcing time
3. Single-phase tests • Mandatory in effectively earth neutral systems. • The main requirements for the test duty are related to: • Breaking of the rated symmetrical short-circuit current with the maximum arcing time and with the recovery voltage based on phase-to-earth voltage • Outer pole under test to simulate the maximum stress in the coupling mechanism
4. Double-earth fault • Mandatory in non-effectively earth neutral systems. • The main requirements for the test duty are related to: • Breaking of the 87% of the rated symmetrical short-circuit current with the maximum arcing time and with the recovery voltage based on phase-to-phase voltage
5. Technology of Vacuum Interrupters • History: • 1896: First analysis of electrical field breakdown in vacuum (theoretical 6MV per 1mm) • 1930: Quantum mechanics describes the field emission in vacuum • 1960: First commercial VI in the market • 2012: Over 75% all MV CB uses VI to switch the current • VIs are currently commercially available up to 145kV. Prototypes of multiple switching units at 220kV or higher voltages are under development. • Development of VIs is continuing towards higher voltages and higher short-circuit currents with the employment of advanced arc control systems.
5. Technology of Vacuum Interrupters • Main feature of VI technology: • High number of operations: Up to 100 of rated short-circuit interruptions and up to 10.000 of rated current interruptions without any maintenance • Compact & Lightweight and High Reliability with extremely low failure rate • Contact materials with low welding tendency and low chopping current • Contact design with arc control for high interrupting capacity and for withstanding fast recovery voltages
6. Extension of the validity of test results • Who?- Manufacturer Experts / Expert teams- Third party Experts • What?- Yes it can be extended / it may be extended- No, it can not be extended • Responsibilityonly manufacturer • Is not the task of test labs or accreditation institutes
7. Conclusion • The design and technology of high-voltage circuit-breakers is continuously developing and will continue also in the future. • Type testsqualify the type of product series while the routine testsensure that the manufactured series are always in accordance with the type tested sample • Circuit-breakers qualified according to the IEC 62271-100 are best suited for switching of short-circuit currents. They are able to switch currents with high asymmetry and fast rising TRVs without any maintenance throughout the lifetime • Most of the failures are due to inappropriate human behaviors either during the project management phase (wrong product definition) or during operations (installation, operation, maintenance, etc.) • Thus, considering additional regulation should not bring more safety. • On the other side deregulating a proven standard will reduce the safety level